Section
02164
TIEBACK
ANCHORS
PART 1 - GENERAL
1.1
THE
REQUIREMENT
A. This section covers
the furnishing, installation, and testing of earth anchors for the
tie-back system.
B. The CONTRACTOR shall
furnish all tools, equipment, materials, and supplies and shall
perform all labor required to complete the Work as indicated in the
Contract Documents and specified herein.
1.2
RELATED
WORK SPECIFIED ELSEWHERE A. Section 02200 Earthwork
B. Section 03300
Cast-in-Place Concrete
C. Division 05 Metals
D. Division 16
Electrical
1.3
REFERENCE
SPECIFICATIONS, CODES AND STANDARDS
A. Comply with the
applicable reference specifications as specified in the GENERAL
REQUIREMENTS.
B. Comply with the
current provisions of the following Codes and Standards.
1. Commercial
Standards:
ACI 318
Building Code Requirements for Reinforced
Concrete
ASTM A 123
Specifications for Zinc (Hot-Dip Galvanized)
Coatings on Iron and Steel Products
ASTM A 153
Specification for Zinc Coating (Hot Dip) on Iron and
Steel Hardware
ASTM A 385
Practice for Providing High-Quality Zinc
Coatings (Hot-Dip)
ASTM A 722
Specification for Uncoated High-Strength Steel
Bar for Prestressing
Concrete
ASTM D 512
Test Methods for Chloride Ion in Water
ASTM D 922
Specification for Non-rigid Vinyl Chloride
Polymer Tubing
PCI
Recommended Practice for Grouting of Post-
Tensioned Concrete
1.4
CONTRACTOR
SUBMITTALS
A. Submittals shall be
made in accordance with the General Requirements.
B. The following
submittals and specific information shall be submitted to
the
ENGINEER.
1. Complete data,
detailed drawings, and installation drawings of the earth anchors
together with all components and accessories including the following
items.
a. A tieback anchor
schedule indicating anchor identification, design load, test load,
lock-off load, type, number, and size of tendon, minimum total
anchor length, minimum bond length, minimum tendon bond length, and
minimum unbonded length for each earth anchor.
b. A drawing of the
tieback anchor tendon and corrosion protection system including
details for spacers to separate elements of the tendons and their
locations, centralizers and their locations, unbonded length
corrosion protection systems, bond length corrosion protection
systems, anchorages and enclosure tubes (trumpets), proper
identification of all welds, anchorage corrosion protection systems,
drilled or formed hole sizes, level of each stage of grouting, any
revisions to structure details necessary to accommodate the earth
anchor system intended for use.
2. The grout mix
design and procedures for placing the grout including reports of
strength test results for trial mixes for the cement-rich grout.
1.5
QUALITY
ASSURANCE
A. The CONTRACTOR
shall provide the services of an ENGINEER, registered in the State
of California, with at least 5 years of experience in the design and
construction of permanently anchored walls. A foreman or
superintendent experienced in the grouting of tiebacks shall be
present while this Work is performed.
B. Drilling operators
and foremen shall have a minimum of 3 years of experience
installing permanent anchors. The CONTRACTOR shall submit
satisfactory documentation that Project personnel have appropriate
qualifications.
C. Mill certificates
shall be submitted to the ENGINEER for the steel tendons. The
certificates shall indicate ultimate load, yield stress, and percent
of elongation at rupture for each heat of prestressing steel.
D. Tieback testing and
lock-off shall be performed by the CONTRACTOR as detailed in the
Contract Documents under the continuous observation of the ENGINEER.
Test results are subject to the acceptance of the ENGINEER, and the
earth anchors are subject to rejection based on the test results.
E. The CONTRACTOR
shall notify “DIGALERT” 48 hours prior to beginning excavation
or drilling operations.
F. The CONTRACTOR
shall furnish a set of As-Built drawings showing all earth
anchors remaining in place upon completion of construction
operations. As-Built drawings shall show length of concrete
embedment, anchor size, length, line and grade of all earth anchors
remaining in place.
PART 2 - PRODUCTS
2.1
MATERIALS
A. Anchor
Rods shall be:
High-strength steel, uncoated; ASTM A 722, Type II
(deformed).Dywidag Systems International "Threadbars,"
Advanced Construction Enterprises "ACE All thread," or
equal.
B. Miscellaneous
Metal Components, Including Enclosure Tubes, Wedge Plates,
Anchor
Plates, Bearing Plates, Couplers, and Nuts:
Carbon steel, hot-dip galvanized after fabrication in conformity
with ASTM A 123, A 153, and A 385.
C. Sheathing,
Including End Cap, Grout Tube, Sealing Cap, and Similar Accessories:
PVC, minimum compressive strength of 50,000 psi, minimum tensile
strength of
7,000 psi; smooth and
corrugated shapes as indicated on the Drawings.
D. Corrosion
Inhibitors:
Mastic; maximum chlorides per ASTM D 512, 10 ppm; maximum
nitrates per ASTM D 922, 10 ppm; maximum sulfides per ALPHA "Sulfide
in Water," 10 ppm. Visconorust 31664 as manufacutered by
PelSeal Technologies, LLC, CORTEC Corporation, Or Equal.
E. Grout
Additive shall be:
Sika "Intraplast N", BASF “Tetraguard AS20” Or Equal.
F. Centralizers and
spacers shall be fabricated from plastic, steel, or material which
is non-detrimental to the prestressing steel. Wood shall not be
used. The centralizer shall be able to support the tendon in the
drill hole and position the tendon so a minimum of 3 inches of grout
cover is provided and shall permit grout to freely flow in the drill
hole. A combination centralizer and spacer may be used.
2.2
GROUT
A. Grout shall be
composed of portland cement, water, aggregate, and an additive as
specified hereinbefore. Cement and water shall be as specified in
Section 03300
Cast-In-Place Concrete.
B. The proportions of
cement, water, aggregate, and additive shall, unless otherwise
specified, conform to manufacturer's recommendations and the
requirements of ACI
318 to produce a
cement-rich grout with a compressive strength of not less than
4,000 psi at 28 days.
Maximum chloride ion content of the grout shall not exceed the
limits of ACI 318, Table 4.5.4.
2.3
FABRICATION
A. Anchorage
and Couplers:
Anchorage components shall develop at least 95 percent of the
minimum ultimate strength of the bar tendon. Couplers shall
develop the minimum ultimate strength of the tendon.
B. Corrosion
Protected Tendons:
Corrosion protection for the tendons shall be as indicated on the
Drawings.
C. Corrective
Retensioning:
Provision for monitoring long-term prestress loss and corrective
retensioning of the anchors shall be as shown on the Plans.
2.4
TENDON
STORAGE AND HANDLING
A. Tendons shall be
handled and stored in such a manner as to avoid damage or corrosion.
Damage to the prestressing steel as a result of abrasions, cuts,
nicks, welds, or weld splatter will be cause for rejection. The
prestressing steel shall be protected if welding is to be performed
in the vicinity. Grounding of welding leads to the prestressing
steel is forbidden. Prestressing steel shall be protected from
dirt, rust, or deleterious substances. If heavy corrosion or pitting
is noted, the ENGINEER shall reject the affected tendons.
B. The CONTRACTOR
shall use care in handling and storing the tendons at the site.
Prior to inserting a
tendon in the drill hole or auger, the CONTRACTOR and the INSPECTOR
shall examine the tendon for damage to the encapsulation and the
sheathing. If, in the opinion of the INSPECTOR, the sheathing has
been damaged, the CONTRACTOR shall repair it with ultra high
molecular weight polyethylene tape. The tape shall be spiral wound
around the tendon to completely seal the damaged
area. The pitch of the
spiral shall ensure a double thickness at all points.
PART 3 - EXECUTION
3.1
INSTALLATION
A. Installation of the
earth anchors shall be in accordance with the instructions,
procedures, and details indicated in the Contract Documents.
B. Drilling:
1. The CONTRACTOR
shall select the drilling method. The drilling method and
procedures shall prevent loss of ground from above and around the
drilled hole. Casing for anchor holes, if used, shall be removed.
The location, inclination, and alignment of the drilled holes shall
be as shown on the Drawings. Inclination and alignment shall be
within 3 degrees of the planned angle at the bearing plate, and
within 12 inches of the planned point of entry.
C. Tendon Placement:
1. Anchor tendons shall
be placed in accordance with manufacturer's recommendations and
secured in place by approved supports. Care shall be taken that
the anchor tendon is centered in the hole for the entire bond
length.
D. Grouting:
1. The anchor load
shall be transferred to the ground by bond. Anchor tendons shall
not be bonded to the ground in the range of the free stressing
length and shall stay permanently free for load checking and any
necessary load adjustments.
2. The grouting
equipment shall be capable of continuous mechanical mixing to
produce a grout free of lumps and undispersed cement. A manifold
system with a series of valves and calibrated pressure gauge
capable of measuring pressures of at least 150 pounds per inch or
twice the actual grout pressures used, whichever is greater, shall
permit continuous circulation and pumping of grout with accurate
control of grout pressure.
3. Grouting operations
shall be in accordance with the PCI "Recommended Practice for
Grouting of Post-Tensioned Concrete" and the manufacturer's
recommendations.
4. Grout shall be
injected at the lowest point of the drilled hole. Grouting shall
proceed such that the hole is filled to prevent air voids. The hole
shall be filled progressively from bottom to 2 feet above the bond
length (attached length).
5. The free length
(unbonded length) shall be filled with a 2-sack cement-sand slurry
as shown on the shop drawings.
3.2
LOAD
MONITORING DEVICES
A. Permanent load
cells shall be furnished and installed at the anchor
locations indicated on the Drawings. The load cells shall be
annular in shape and hermetically sealed, with the center hole of
adequate size to accommodate the tendon. The tendon shall be
concentrically located in the annular space and the axes of the
tendon and load cell shall be parallel to prevent eccentric loading.
B. All necessary
hardware and/or adapters required by the manufacturer for proper
functioning of the load cells shall be provided. Permanent load
cells shall be installed after all required tests have been
successfully performed on the anchor. The capacity of each load
cell shall be at least 125 percent of the design load.
C. Weatherproof and
waterproof terminal boxes and conduit to group instrument leads
shall be furnished and installed at the locations indicated on the
drawings.
D. Load cells shall be
as manufactured by: Transducers, Inc.
P.O. BOX 3344
Sedona,
Arizona 86340
Phone:
(800) 398-6481,
Geokon Incorporated
48
Spencer Street
Lebanon,
NH 03776,
Or Equal.
3.3
STRESSING
AND TESTING
A. Anchor
Stressing:
Stressing shall not start before the grout and the
adjacent concrete lagging has reached a minimum compressive strength
of 3,500 psi and
1,000 psi, respectively,
and has set for at least 3 days after its placement in the drilled
hole. A minimum of three grout cubes and concrete cylinders must
have been tested and two must have reached the specified strength.
Test reports shall be submitted to the ENGINEER for acceptance prior
to stressing.
B. Testing
of Anchors:
The design capacities of all tiebacks shall be verified by a
program of proof tests, performance tests, and creep tests.
1. The CONTRACTOR
shall provide all equipment and instrumentation necessary for
verification of the adequacy of the earth anchors.
a. A dial gauge with
tripod support and capable of measuring displacements to
0.001 inch precision and
having 6 inches of travel shall be used to measure earth anchor
movement.
b. A hydraulic jack
and pump shall be used to apply the test load. The jack and
calibrated pressure gauge shall be used to measure the applied load.
The hydraulic jack capacity shall be at least 250 percent of the
earth anchor design load. The pressure gauge shall be graduated in
100 psi increments or less. The load shall be applied
incrementally. The load shall be raised or lowered from one
increment to another as shown on the plans.
c. The stressing
equipment shall be placed over the anchor tendon in such a manner
that the jack, bearing plate, and stressing anchorage are axially
aligned with the tendon and the tendon is centered within the
equipment.
2. Load sequencing for
anchor testing and acceptance criteria for test results shall be as
indicated on the plans.
3. If the load test
results are acceptable to the ENGINEER, the earth anchor shall be
locked-off at no less than 110 percent of the rated design load.
a. The earth anchor
may be completely unloaded prior to lock-off.
b. After transferring
the load and prior to removing the jack, a lift-off reading shall be
made.
c. The lift-off load
shall be within 10 percent of the required lock-off load (110
percent of design load); if not, the anchorage shall be reset, and
the lift-off measurement repeated until an acceptable reading is
obtained.
4. If the load test
results are not acceptable to the ENGINEER, the earth anchor shall
be replaced as directed by the ENGINEER.
5. For temporary
tieback anchor installation, the number of anchors tested to the
200 percent design load
shall be determined by the ENGINEER; however, a minimum
of 2 percent of the anchors at each level shall be
tested to the
200 percent load and
held at a constant tension for a period of time not less than
24 hours. Once the
loading for 200 percent of the design load is reached, the axial
extension of the anchor assembly shall not exceed 1/2 inch. An
axial extension exceeding 1 inch is considered as failure,
while axial extensions ranging from 1/2 inch to 1 inch may be
assigned partial capacity ratings subject to approval of the
Structural Engineer licensed in the State of California responsible
for the design of the shoring system and the ENGINEER. The total
axial anchor extension,
measured form the time of initial load application to the
termination of the 200
percent load shall not exceed 4 inches. If the total axial
extension of the anchor exceeds 4 inches, the ENGINEER may down rate
or reject the anchor as unacceptable.
6. All remaining
tieback anchors shall be proof tested to a least 150 percent of the
design load. Any proof-tested anchor with axial extension exceeding
0.1 inch after 15 minutes under 150 percent of design load or a total
axial extension exceeding 4 inches from initial application of load
to termination of the test may be down rated or rejected by the
ENGINEER.
7. The CONTRACTOR shall
submit anchor-testing procedures to the ENGINEER
for acceptance prior to
installation of any temporary tieback anchors.
8. Grouted anchors that
depend on the maintenance of high grout pressures for their design
capacity shall not be permitted.